Doug Ritter (Texrbama)
Registered Member Username: Texrbama
Post Number: 32 Registered: 3-2007 Posted From: 70.5.74.192
Rating: N/A Votes: 0 (Vote!) | Posted on Saturday, August 18, 2007 - 9:03 pm: | |
When you say cuts in and out, does the unit shut down or just the compressor. If just the compressor then it may be the t-stat or the compressor overload. Pray that it's the t-stat. The t-stat may be on its last leg or may be something as simple as a loose wire on the control side of the unit. First check all connections from start to finish. Be sure that you have no a/c power on the unit during this check. The t-stat has a differential pre. set points. Meaning, the t-stat will cycle somewhere between 4-6 degrees. The t-stat has a capillary tub that is pre-charged from the factory with the same refrigerant as your a/c., R-22 if an older unit. If the carpellary have lost its charge or, losing its charge this will cause your problem. A new t-stat is cheap and easy to replace. You may be able to pick one up at your local wholesale refrigeration part’s store. As far as the location of the t-state, you should be able to see it on the face of the unit unless you have a remote wall mount t-stat. I hope this adds light to your problem. |